请问这种带连廊的布局算前室还是合用前室

请问这种带连廊的布局算前室还是合用前室

尼好吗 | 2024-12-13 16:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

jinyanwu 2024-12-14 11:12 00 [回复]举报

个人意见,仅供参考:

根据《建筑防烟排烟系统技术标准 GB51251-2017》:

前室是有明确定义的。

都是独立前室,包括左边那个消防电梯的应该也不是合用前室。

cala 2024-12-14 11:45 10 [回复]举报

个人理解同上:连廊作为楼梯的前室,左侧前室仅为消防电梯使用,仅为消防电梯前室。

wetom 2024-12-16 12:31 00 [回复]举报

个人理解,就是合用前室,如果连廊做楼梯的前室,变成前室穿套了。

vicher 2024-12-16 15:26 00 [回复]举报

个人理解:楼梯需经消防电梯前室入户,所以电梯前室为合用前室;连廊作为楼梯前室,存在前室穿套的问题。