消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

无窗房间装修材料耐火级别讨论

建筑内部装修设计防火规范》GB50222-2017第4.0.8条:无窗房间内部装修材料的燃烧性能等级除A级外,应在表5.1.1、表5.2.1、表5.3.1、表6.0.1、表6.0.5规定的基础上提高一级。还要强制满足吗?室内装修是不是满足《建筑防火通用规范》GB 55037—2022第6.5条就可以,6.5条文里没有规定无窗房间墙顶地都要A级材料啊?


sufi | 2024-11-14 09:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

我头发贼黑 2024-11-14 09:31 00 [回复]举报

jinyanwu 2024-11-14 10:52 00 [回复]举报

只是现在不再规定无窗了,但根据具体场所分开进行了规定,如歌舞娱乐场所,最低也是A+B1了:

根据使用性质,当使用这些场所时,对应相关条款就行了。有的严了,有的有所放松。

通规只是废止了相关规范条款的强制性,只要不违反通规上条款相关要求,对于废止的条款,还是可以作为一般条款参考使用的;

sufi   回复: jinyanwu2024-11-14 11:34

学习了,感谢回答。

0    0 [回复]举报

小唐12321 2024-11-14 11:16 00 [回复]举报

这种问当地消防部门啊,要你执行你也没办法

江苏刚刚好 2024-11-15 07:40 00 [回复]举报

《建筑防火通用规范》GB 55037—20222只是废止了《建筑内部装修设计防火规范》GB50222-2017第4.0.8条的“强制性条文属性”,在《建筑内部装修设计防火规范》GB50222-2017修订以前,相关条文转为推荐性条文,推荐性条文的执行原则是推荐性标准作为设计依据时,其推荐性条件仍需执行。比如《建筑内部装修设计防火规范》GB50222-2017第4.0.8条的“地上建筑的水平疏散走道和安全出口的门厅,其顶棚应采用A级装修材料,其他部位应采用不低于B1级的装修材料”这条规定也已经被《建筑防火通用规范》GB 55037—20222废止了“强制性条文属性”,但实际设计中疏散走道的顶棚仍需要采用A级装修材料。

关闭

关闭

手机APP下载