消防问答 > 建筑防火 提问

设置化学品安全柜的房间,还要做建筑泄压吗?

各位老师好,一个化学实验室的一个房间,里面的化学品放置在安全柜里,那么,这个房间要做轻质泄压墙做建筑泄爆吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 5 回答

安洪全 24-02-05

应该不用吧,实验室即使有危险品,量应该也不大,不会对建筑结构造成影响。

0 0 [回复]举报

我是小鱼鱼   回复: 安洪全24-02-05

谢谢!但是,电气专业划分了爆炸危险区,我们建筑专业不用泄爆了吗?

0 0 [回复]举报

安洪全   回复: 我是小鱼鱼24-02-05

要是有其他专业提了,我觉得就得按爆炸区域考虑了

0 0 [回复]举报

我是小鱼鱼   回复: 安洪全24-02-06

谢谢反贼老师。

0 0 [回复]举报

LRLR 24-03-01

只要划了爆炸危险区域,就要轻质泄爆墙体或屋顶

至于有没有爆炸危险区,参考GB50058,不过一般的化学实验室不划,但专用于储存危险化学品的房间,

除非能满足 可不按物质危险特性确定生产火灾危险性类别的最大允许量 表格的要求,否则就应该划爆炸危险区域,和有无试剂柜没关系

0 0 [回复]举报

最新问题

关闭

关闭