磷酸铁锂电池的存放和安装消防要求

1、需要使用磷酸铁锂电池作为原材料生产,存储的仓库最低按照丙类库设置,但相应的消防设备设施选用哪种最合适?一旦电池热失衡出现火险,如何迅速扑救且不会造成蔓延,影响库内其他电池?

2、电池组装过程中的搬运使用哪种设备最安全且有效率?或者有哪种设备可以帮助人员搬运和组装作业?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 1 回答

安洪全 23-06-02

您可以参考“预制舱式磷酸铁锂电池储能电站消防技术规范 T/CEC373-2020”这本规范


0 0 [回复]举报