消防问答 > 建筑防火 提问

与注2的防火墙的区别是,此处的防火墙上是有门窗洞口的。

3 两座一、二级耐火等级的厂房,当相邻较低一面外墙为防火墙且较低一座厂房的屋顶无天窗,屋顶的耐火极限不低于1.00h,或相邻较高一面外墙的门、窗等开口部位设置甲级防火门、窗或防火分隔水幕或按本规范第6.5.3条的规定设置防火卷帘时,甲、乙类厂房之间的防火间距不应小于6m;丙、丁、戊类厂房之间的防火间距不应小于4m。

问:该处较高一面外墙,需要设置为防火墙吗?

与注2的防火墙的区别是,此处防火墙上是有门窗洞口的。

根据6.1.5的条文说明(对于因防火间距不足而需设置的防火墙,不应开设门窗洞口。必须设置的开口要符合本规范有关防火间距的规定。)

请问以上蓝色标注,必须设置开口时,具体指的是要符合什么规定?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

工程新一 21-08-16

问的好,你上一问“较高一面外墙”确实不需要设置防火墙,可参照图集

后面的条文说明有点绕,规范说的不是很清楚,我个人的理解是防火墙只要开口部位满足防火分隔的要求,则可以按照3.4.1条的规定减少防火间距

0 0 [回复]举报

sewenlook   回复: 工程新一21-08-18

两座一、二级耐火等级的厂房,当相邻较高一面外墙的门、窗等开口部位设置甲级防火门、窗或防火分隔水幕或按本规范第6.5.3条的规定设置防火卷帘时,甲、乙类厂房之间的防火间距不应小于6m;丙、丁、戊类厂房之间的防火间距不应小于4m。


是否可这样理解,如果较高一面外墙没有门窗洞口,丙、丁、戊类厂房之间的防火间距不应小于4m。
这个外墙是否要耐火极限大于0.5小时,以满足二级耐火等级厂房要求。



0 0 [回复]举报

工程新一   回复: sewenlook21-08-18

是的

0 0 [回复]举报

最新问题

关闭

关闭