消防问答 > 气体灭火 提问

关于民用建筑的网络机房是否应当设置气体灭火?

根据《数据中心设计规范》第3.1.2、3.1.3、3.1.4条规定,民用建筑内的网络机房应当归类为c级机房且根据《建筑设计防火规范》第8.3.9条规定未见要求民用建筑内配套的网络机房应该设置气体灭火。那我想问,民用建筑内配套的网络机房因为大多为电子设备,不考虑用水的灭火系统,可否采用干粉吊球和灭火器进行灭火呢?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

刘丽波 21-07-24

如设置网络机房的建筑依《建规》需要设置自动灭火设施,此房间依《数据中心设计规范》13.1.3执行,设置何种系统主要看数据的重要程度。

干粉吊球属于自动灭火设施,灭火器属于手动灭火设施。灭火器都需要设置,干粉灭火没有防复燃功能,不建议使用。

3 0 [回复]举报

潘天坤 24-06-30

从建规GB50016来说,C级别电子信息系统机房的主机房不需要设置自动灭火系统

不过按照数据中心设计规范 GB50174-2017第13.1.3条规定: C级数据中心的主机房宜设置气体灭火系统,也可设置细水雾灭火系统或自动喷水灭火系统

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

0 0 [回复]举报

最新问题

关闭

关闭