DN25管上下喷算一个喷头吗

验收方提出DN25只能带一个喷头,吊顶内大于800mm设置上下喷DN25管不符合规范吗?

岳飞 | 2024-10-22 20:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

缱绻一夏 2024-10-23 08:55 00 [回复]举报

符合

资源网小助理 2024-10-23 09:40 00 [回复]举报

设计流量已经确定了,上下喷只算一个

LHH2737 2024-10-23 09:40 10 [回复]举报

符合,这个验收方乱讲的,

同时设有上下喷时,只需要按最多的那一侧计算喷头数量即可,两边都是1个那就是1个不需要相加

张治福 2024-10-23 16:46 00 [回复]举报

在同一处设置上下喷哦,而不是DN25的管子后面,设下喷隔一段距离又设置1个上喷哦。