消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

如果在排烟风井满足耐火极限要求,密封都没问题,在设置镀锌钢板排烟管是否需要防火措施


假设可以利用土建排烟风井,排烟风井耐火极限能满足1h,只是因为内壁不太光滑在用镀锌钢板安装风管是否会被认为是在管井中设置了排烟管道,还要在做防火包裹的措施的。如下:


根据《建筑防烟排烟系统技术标准》 (GB51251-2017)第4.4.8.2条及 暖通施工通用说明第二.2.2)条:竖向设置的排烟管道应设置在独立的管道井内,排烟管道的耐火极限不应低于0.5h。

EQS | 2024-10-11 00:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

潘天坤 2024-10-11 08:42 00 [回复]举报

从规范角度来说,此处有不低于0.5小时耐火极限要求


STON 2024-10-11 08:45 20 [回复]举报

《通用规范》竖井没做强制性要求,可以和设计沟通下,我理解,实在有困难都可以不做(风管和保温)。竖井粉刷光滑等措施。

《通规》11.1.3 机械加压送风管道和机械排烟管道均应采用不燃性材料,且管道的内表面应光滑,管道的密闭性能应满足火灾时加压送风或排烟的要求。


《51251-2017》4.4.7 机械排烟系统应采用管道排烟,且不应采用土建风道。排烟管道应采用不燃材料制作且内壁应光滑。当排烟管道内壁为金属时,管道设计风速不应大于20m/s;当排烟管道内壁为非金属时,管道设计风速不应大于15m/s;排烟管道的厚度应按现行国家标准《通风与空调工程施工质量验收规范》GB 50243的有关规定执行。

磊中 2024-10-11 09:04 10 [回复]举报

这里是不用再做防火包裹了,这里可以看做整体的管道井,耐火极限达到要求就可以了

关闭

关闭

手机APP下载