排烟口排烟阀必须要设置手动装置吗?

我们单位有四个水流指示器,三个末端试水装置,四个排烟风机,但只有一个排烟风机控制柜。请问,我们单位只有一个防火分区设置了排烟系统吗?谢谢

阿进 | 2024-10-06 01:11
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

赵晓亮 2024-10-07 08:22 00 [回复]举报

你好,建筑防烟排烟系统技术标准 GB51251-2017 中4.4.12的第5款,有明确规定,请确认。

张治福 2024-10-08 08:21 00 [回复]举报

是需要设置手动操作装置的,但常开式排烟口不用

潘天坤 2024-10-08 09:05 00 [回复]举报

常开排烟口就是普通排烟口,不需要手动控制装置

地上排烟系统一般按照防烟分区考虑,当然仅负担一个防烟分区的情况属于比较特殊的

磊中 2024-10-08 16:54 00 [回复]举报

首先四个水流指示器应该有四个末端试水装置或者三个末端试水装置加一个水流指示器相对应区域的最不利点装试水阀。

其次,这里是四台风机,应该是四个防火分区都设置了排烟系统,只是公用一个风机控制柜,这个也是可以的。

最后就是排烟口,常开排烟口不用设置手动装置