单多层建筑需要设置消防车登高操作场地吗?

《建筑防火通用规范)第3.4.6条高层建筑应至少沿其一条长边设置消防车登高操作场地。未连续布置的消防车登高操作场地,应保证消防车的救援作业范围能覆盖该建筑的全部消防扑救面。

根据此条文是否可以默认单多层建筑无需设置消防车登高操作场地?

不懂111 | 2024-09-12 09:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友68723 2024-09-12 11:20 01 [回复]举报

单多层也要设,条文解释:3.4.6 本条规定了高层工业与民用建筑设置消防车登高操作地的基本要求。

    任何建筑在建设时均应充分考虑消防车到场开展消防救援的需要,使建筑周围具有必要的开阔场地,具备与建筑高度、规模和火灾危险性相适应的消防救援条件。在建筑使用时,要保证这些场地不会被占用。消防车登高操作场地对于保障消防车到场后迅速对高层建筑展开消防救援行动发挥重要作用,其布置应结合建筑的外形和立面、建筑的高度等情况确定。

我头发贼黑 2024-09-12 14:24 00 [回复]举报

55037实施指南:3.4.6 单层和多层工业与民用建筑以及地下建筑不严格要求设置消防车登高操作场地,但仍要视建筑的火灾危险性和火灾 扑救需要设置与否, 如多层的大型丙类仓库、 物流建筑和丙类厂房,大型的商业综合体、大型的地下建筑等。

phone0224 2024-09-13 11:12 00 [回复]举报

从符合规范角度,单多层不设消防车等到操作场地是不违反规范的。从实际使用角度,如果有条件还是建议设置。