消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

一类高层建筑高位水箱必须设稳压装置吗?

一类高层建筑高位消防水箱最低水位与最不利点室内消火栓、自喷系统高差满足不了静压要求,水箱间必须设置稳压泵吗?如果系统是临时高压系统,管网压力能满足最不利点消防用水,高位消防水箱可以不设稳压泵吗?(我个人认为必须设,因为临时高压系统管网压力不能时时保证最不利点火灾初期水压)。

消防网友18336 | 2024-08-16 14:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防检查 2024-08-16 15:49 10 [回复]举报

当水箱的容积满足要求,最低有效水位能满足最不利点的静压,我感觉就够了,可以不设稳压泵。稳压泵只是维持管网内的静压的,真有初期火的时候,满足静压和水量的水箱就够了,再发展,后续的水量和压力就是消防水池和消防水泵供给了。

布泽德 2024-08-17 09:18 00 [回复]举报

临时高压系统高差不能满足静压要求,那只能上稳压泵。如果满足静压要求,可以不设稳压系统。

关闭

关闭

手机APP下载