消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

多个一类高层大型商场内部建筑互不联通,可以用设立一个主监控室室采用集中控制报警系统模式嘛?

如题,分监控室打算不安排消防值班人员。主监控室安排24小时双岗值班。分监控室把联动控制线路和高压细水雾、固定消防炮等子系统控制功能全部接入主监控室内。整个系统做成集中控制报警系统模式。可以吗?


消防网友23355 | 2024-08-06 18:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

君艺 2024-08-07 08:55 00 [回复]举报

如果是一家单位,肯定没有问题。

王的MIX4 2024-08-07 14:23 00 [回复]举报

这个模式就属于日常中的产权较多,统一管理,是允许的

南明离火 2024-08-10 08:37 00 [回复]举报

很可以

关闭

关闭

手机APP下载