关于储烟仓问题

烟规规定,储烟仓高度是层高的10%或20%,这个是不是最低规定啊,储烟仓高度不能低于这个但可以更高,还是说这是一个固定的数值不能变的?

花生12138 | 2024-07-18 09:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

LHH2737 2024-07-18 11:21 00 [回复]举报

规范的储烟仓厚度是最低规定,同时设计清晰高度也有最低规定,一般为2.1m,考虑储烟仓厚度时也要考虑不能影响最小的设计清晰高度

消防检查 2024-07-18 11:36 00 [回复]举报

最低值。

缱绻一夏 2024-07-18 13:31 00 [回复]举报

是可以变得,但是储烟仓的厚度不能高于最小清晰高度,且储烟仓的厚度也影响本防烟分区的单个排烟风口最大排烟量的限值,可以根据实际情况合理设计

潘天坤   回复: 缱绻一夏2024-07-19 06:59

烟层厚度不等同于储烟仓高度,控制排烟口上排、下排及距地高度才是关键,不过一般加大储烟仓高度之后烟层厚度会相对应增加

0    0 [回复]举报

缱绻一夏   回复: 潘天坤2024-07-19 10:42

是的,老师很专业!

0    0 [回复]举报

潘天坤 2024-07-18 18:08 00 [回复]举报

一般来说,满足空间净高及最小清晰高度要求的前提下可以提高储烟仓高度要求

规范有对不同排烟方式下的储烟仓厚度作出一些要求,一般不低于就符合规范要求,如果想适当提高又满足空间净高及最小清晰高度要求是没问题的