开业前消防安全检查与住建审核验收适用规范不同怎么办?

公众聚集场所,在办理消防设计审核、验收时,适用的是《建筑设计防火规范 GB50016-2014(2018年版)》。验收后,单位申报开业前消防安全检查时,《建筑防火通用规范 GB55037-2022》实施,请问,在办理安检时应该参照什么规范进行审批(应该如何处理)?

爱你没商量 | 2024-05-24 10:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

倜圳 2024-05-24 11:17 00 [回复]举报

中华人民共和国公安部第119号令 第一章第六条

南明离火 2024-05-24 16:19 00 [回复]举报

按图施工 按图检测 按图验收  

梅有名 2024-05-26 12:29 00 [回复]举报

正常的开业前检查查的是你消防安全管理资料,其实根本不涉及原设计规范。但现实情况中消防验收归住建后,消防部门对住建部门的验收并不放心,所以要再查一遍,遇到你的情况,你应当向消防机构出具你的建设工程在《建筑防火通用规范》实施前就已经完成消防设计的证据,如施工图审核合格书、消防设计审查意见书等,当然你的场所如果没有通过消防验收就直接申报开业前检查,虽然程序合规,但就是让你执行昨天刚刚执行的新规范人家也有道理,谁让你没过消防验收呢。


潘天坤 2024-06-16 16:06 00 [回复]举报

开业前的检查这些,一般是执行不低于建成年限的标准。

如果有条件,鼓励按照现行规范执行。

如果不具备条件,那么执行不低于建成年限标准即可,当然某些特别的规定除外(例如近期出台的中小学校、幼儿园消防安全十项规定提出了消防设施要求,这个比较容易满足,也能提高使用安全)。