关于建筑疏散走道的应急照明设置问题。

火通规里将建规里的需要设置疏散照明的位置:4公共建筑内的疏散走道进行了废止,在火通规里没有提出公共建筑的疏散走道需要设置,仅仅提出了疏散走道的照度要求。那公共建筑的疏散走道未设置疏散照明的此类隐患的引用条款该取哪条呢?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防检查 2024-05-13 14:08 00 [回复]举报

确实火通规里没有提及“疏散走道”,但仍可引用建规的10.3.1,废止的是“强条”属性。“疏散走道”不设疏散照明不现实,属于疏散重要路径,而且火通规还对照度提出了要求。

冰冷的风 2024-05-16 16:01 00 [回复]举报

其实我们做设计的时候,可以从实际角度出发,如果发生事故,走道一片漆黑,那么设置应急照明系统的意义在哪里?

潘天坤 2024-06-03 16:15 00 [回复]举报

1、《建筑防火通用规范》(GB55037-2022)正文关于疏散照明设置的条件确实缺少了疏散走道,然后实施指南有提到“本条规定应设置疏散照明的部位,是建筑内人员在疏散时必须经过的主要路径和节点,如疏散出口、疏散走道和疏散通道等”。虽然说实施指南效力小于规范正文,这边可以辅助理解。

2、疏散走道未设置疏散照明,可以按照无法满足照度要求提(没有设置疏散照明,所以疏散照明的地面最低水平照度不满足规范要求),同时也可以结合《建筑设计防火规范》(GB50016-2014)(2018年版)关于疏散照明设置条件一起提出。

违反《建筑设计防火规范》(GB50016-2014)(2018年版)第10.3.1条规定及《建筑防火通用规范》(GB55037-2022)第10.1.10条第2款规定。