有烟感一定要配喷淋吗

有烟感一定要配喷淋吗

??? | 2024-05-02 13:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

花生12138 2024-05-04 11:30 00 [回复]举报

不一定,看具体是什么场所,详见建规8.3和8.4

雄哥 2024-05-04 15:19 00 [回复]举报

     不一定,各种场所需要设置什么消防设施规范都要规定,大部分设置自动报警的场所都需要设置喷淋。但有些设置防排烟或其他设施需要与自动报警系统联动的场所,可能不需要设施自动喷淋系统,但需要设置自动报警系统,另外,有些场所不适宜用水灭火,可能需要设置自动报警系统,但不能设置自动喷淋系统。

      


         希望对你有帮助

那年的你 2024-05-05 07:31 00 [回复]举报

不一定。

南明离火 2024-05-05 08:33 00 [回复]举报

各自独立条件

安洪全 2024-05-06 08:42 00 [回复]举报

不是充要条件,各有各的配置要求

gx祥子 2024-05-06 08:51 00 [回复]举报

有烟感说明有火灾自动报警系统,符合有火灾自动报警的设置场所要求。不一定符合设置喷淋的场所要求。

戊二烯 2024-05-06 10:08 00 [回复]举报

一、《建筑防火通用规范》 GB55037-2022 8.1.9条   除建筑内的游泳池、浴池、溜冰场可不设置自动灭火系统外,下列民用建筑、场所和平时使用的人民防空工程应设置自动灭火系统:……

二、《建筑防火通用规范》 GB55037-2022 8.3.2条  下列民用建筑或场所应设置火灾自动报警系统:……

————