消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

泡沫灭火装置水泵接合器

露天油罐区设置了泡沫灭火系统,需不需要设置水泵接合器?

chaiyanlei | 2024-04-23 15:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

CN88 2024-04-24 14:46 11 [回复]举报

需要。


消防给水及消火栓系统技术规范 GB50974-2014

5.4.2 自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统和固定消防炮灭火系统等水灭火系统,均应设置消防水泵接合器。

冀A林   回复: CN882024-04-25 16:21

你见过哪个罐区设水泵接合器?

0    0 [回复]举报

安洪全 2024-04-24 14:52 00 [回复]举报

需要

泡沫灭火系统技术标准 GB50151-2021

9.1.4 泡沫灭火系统施工前应具备下列技术资料:    

1 有效的施工图设计文件;    

2 主要组件的安装使用说明书;     3 泡沫产生装置、泡沫比例混合器(装置)、泡沫液储罐、电机或柴油机及其拖动的泡沫消防水泵、盛装100%型水成膜泡沫液的压力储罐、动力瓶组及驱动装置、报警阀组、压力开关、水流指示器、水泵接合器、泡沫消火栓箱、泡沫消火栓、阀门、压力表、管道过滤器、金属软管、泡沫液、管材及管件等系统组件和材料应具备通过了自愿性认证或检验的有效证明文件和产品出厂合格证。

关闭

关闭

手机APP下载