消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防稳压泵的火灾报警联动控制要求

消防稳压泵的火灾报警联动控制要求是怎样的,联锁启停条件有哪些?

wangh6 | 2021-02-25 10:36
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

消防打工人 2021-02-26 14:46 50 [回复]举报

火灾报警联动控制只针对消火栓泵、喷淋泵等灭火应急供水泵。稳压泵的作用是日常维持管网压力,不通过报警系统联动控制,而是通过电接点压力表来控制,当管网压力低于电接点压力表设定的低压值时启动稳压泵,当管网压力高于电接点压力表设定的高压值时停止稳压泵。

wangh6   回复: 消防打工人2021-05-14 16:28

感谢回答

0    0 [回复]举报

关闭

关闭

手机APP下载