消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

喷淋泵起泵,所有分区延迟器下方喷水

如果未发生火灾的情况下,我打开试警铃阀,这时压力开关动作,喷淋泵起泵,这个时候其他分区报警管路延迟器下方在喷水,这个现象是正常的吗?

钟马德 | 2024-03-27 11:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

牛疼 2024-03-28 09:01 00 [回复]举报

正常

一路向西 2024-03-28 09:52 00 [回复]举报

不正常,其他分区报警阀阀瓣不开、警铃试验阀不开,就不应该出水。

同同不同   回复: 一路向西2024-03-29 09:03

正常,消防泵功率扬程较大或启动时间较长的话必然导致阀前压力大于所有阀后压力,阀瓣会打开,而报警管路阀门是常开的,延迟器走水正常

1    0 [回复]举报

zyx562431699 2024-03-28 16:03 20 [回复]举报

启泵后,其他报警阀组系统侧因压力过高阀瓣会短暂打开,水进入延迟器,造成延迟器滴水,如果阀瓣完全打开,会造成延迟器喷水直至充满水。严格来说是不正常的,但实际经常出现这种情况,并没有好的解决办法。有的时候稳压泵启动就能造成阀瓣误开启。

峨溪钓叟 2024-03-31 12:07 00 [回复]举报

应该是正常的。启泵后,有可能有少量的水进入报警管路,延迟器的截流孔会泄水,但是水力警铃不应该响。

许小松 2024-04-01 22:46 00 [回复]举报

不正常,这个是分区控制,而不是所有警铃都响

shawu 2024-04-13 11:37 00 [回复]举报

报警阀的水源侧压力波动小时(如稳泵增压时或系统渗漏)靠报警阀的补偿器吸收波动,如果压力波动大时(如喷淋泵启动时)则会靠主阀瓣开启后经过延迟器排水,但是这些必须是短暂的压力波动;正常工作时系统侧维持在稳压泵停泵压力(因补偿器止回作用),水源侧压力要比系统侧压力大1.16倍才能开启报警阀主阀瓣,如果稳压泵维持的管网压力与打开试警铃后喷淋泵的启动管网压力(小流量导致的泵的扬程增大,但比零流量时的扬程要低)相差不是特别大,,此时其他报警阀的延迟器不会有水流出。

关闭

关闭

手机APP下载