上下喷头算个数

比如我原来的管径DN50,后面带了8个上喷,现在二装后要做上下喷,就等于二装后是8个上喷8个下喷。

上下喷头算个数。

消防陈工 | 2024-03-10 20:47
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

南明离火 2024-03-11 15:30 00 [回复]举报

算单侧,上喷数量,下喷数量 取大值

阿龙 2024-03-11 17:30 00 [回复]举报

按管径带喷头数的话,上下按1个喷头算,按工程量的话按2个算,因为火灾时只会是吊顶内或者吊顶下着火,不会同时着火。根据自动喷水系统设计规范8.0.8 配水管两侧每根配水支管控制的标准流量洒水喷头数量,轻危险级、中危险级场所不应超过8只,同时在吊顶上下设置喷头的配水支管,上下侧均不应超过8只。

2024-03-11 18:00 10 [回复]举报

同时设置上下喷只算一个,规范如下:


heihei 2024-03-12 07:39 00 [回复]举报

上下只算多的一侧,只计算多的一侧喷头即可

梅有名 2024-03-30 17:28 00 [回复]举报

上、下按一个算,因为喷头动作时,不可能上、下一起喷,只能从一边喷,所以算一个