商场店铺仓库防火门开启方向不限?

商场店铺的仓库一般面积小,理货人员少,按照防火规范平均人数不超过30人的房间,是否店铺内的仓库防火门开启方向不限

晴天雨 | 2024-03-04 20:42
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2024-03-05 14:51 00 [回复]举报

可以


建筑防火通用规范 GB55037-2022

7.1.6 除设置在丙、丁、戊类仓库首层靠墙外侧的推拉门或卷帘门可用于疏散门外,疏散出口门应为平开门或在火灾时具有平开功能的门,且下列场所或部位的疏散出口门应向疏散方向开启:    

1 甲、乙类生产场所;    

2 甲、乙类物质的储存场所;   

3 平时使用的人民防空工程中的公共场所;    

4 其他建筑中使用人数大于60人的房间或每樘门的平均疏散人数大于30人的房间;    

5 疏散楼梯间及其前室的门;    

6 室内通向室外疏散楼梯的门。