未安装消火栓泵的场所是否要安装消火栓按钮

银行营业厅建筑面积约200m²设有壁挂式火灾报警控制器1台,室内消火栓系统采用市政供水无消火栓泵,室内消火栓箱内是否必须安装消火栓按钮,若需安装消火栓按钮其安装的意义是什么?

山城老头 | 2024-01-26 14:49
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

懒得说 2024-01-27 13:41 00 [回复]举报

可以不做,做了也只是作为报警按钮

崔晓 2024-01-27 19:02 00 [回复]举报

消火栓按钮不只是启泵的作用,理论上说还有手动报警按钮的作用。我个人认为还有一个就是让消防控制室知道下消防人员在何处救火的作用,便于指挥救援工作。所以觉得启泵按钮不是没有意义的。

江上烟波 2024-01-28 10:11 10 [回复]举报

消火栓按钮的作用一是联锁启动消防水泵、二是和手动火灾报警按钮同样的报告火灾位置的作用。如现场设置有火灾报警按钮,则无需再设消火栓按钮。

marccody 2024-01-29 09:48 00 [回复]举报

《火报设计规范》4.3中,条文解释:消火栓按钮与手动火灾报警按钮的使用目的不同,不能互相替代。稳高压系统中,虽然不需要消火栓按钮启动消防泵,但消火栓按钮给出的使用消火栓位置的报警信息是十分必要的,因此稳高压系统中,消火栓按钮也是不能省略的。