消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

机械排烟和自然排烟能同时采用吗?

在宾馆的疏散走道上,能同时采用机械排烟和自然排烟吗?

与笑同行 | 2023-12-18 09:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

yizhongdayang 2023-12-18 11:04 00 [回复]举报

《建筑防烟排烟系统技术标准》GB51251-2017/4.1.2 同一个防烟分区应采用同一种排烟方式。

whale 2023-12-18 11:08 00 [回复]举报

同一个防烟分区应采用同一种排烟方式,同一防火分区的不同防烟分区尽量采用同一种排烟方式。

如果走道机械排烟,开向走道的大于100平的房间用自然排烟是可以的。

下图是河南这边要求。

阳明心 2023-12-19 08:48 20 [回复]举报

如果同时采用机械排烟和自然排烟,自然排烟窗就变成补风口,而不是排烟了

羊肉串尼 2023-12-27 14:12 00 [回复]举报

把做机械排烟的区域和自然排烟的区域分成两个防烟分区,挡烟垂壁做到位

潘天坤 2024-06-18 12:14 00 [回复]举报

同一个防烟分区只能采取一种排烟方式,如果有多个防烟分区那么每个防烟分区可以采用任意排烟方式,只要符合规范要求即可

关闭

关闭

手机APP下载