消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消火栓泵自动启泵

请问设置了低压压力开关启动消火栓泵,屋顶试验消火栓处放水规定多久启动消火栓泵?

ZFX | 2023-12-13 20:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

泡泡_B9G3 2023-12-14 09:05 00 [回复]举报

达到设定的低压压力开关值,水泵不就启动了么。只有末端放水五分钟水泵启动。

ZFX   回复: 泡泡_B9G32023-12-14 09:58

嗯,管网很大,放到设定值需要很久,低压压力开关设定值最高可以调到多少有说法不?

0    0 [回复]举报

尤里奥洛夫 2023-12-17 21:32 20 [回复]举报

按规范来说,5min是机械应急启动,2min是自动启动,所以我认为是2

ZFX   回复: 尤里奥洛夫2023-12-19 14:25

我也认为可能是2,设置它的目的就是为了及时启泵嘛

0    0 [回复]举报

ZFX   回复: 尤里奥洛夫2023-12-19 14:32

这个2分钟是从低压压力开关动作到启泵的时间开算?还是总的喔?

0    0 [回复]举报

卡卡拉   回复: ZFX2023-12-26 10:18

消防给水及消火栓系统技术规范 GB50974-2014 

11.0.3 消防水泵应确保从接到启泵信号到水泵正常运转的自动启动时间不应大于2min 。

此2min包括主泵故障备泵启动到正常运转时间

0    0 [回复]举报

潘天坤 2025-02-21 21:17 00 [回复]举报

国家技术标准中没有提到这项内容,个别省份(例如广州)技术文件有提到:试验消火栓动作时,消防水泵应在2分钟内自动启动,其他地区可能要看区域内是否有相关要求


关闭

关闭

手机APP下载