4.6.3-3与4.6.3-4自然排烟部分怎么理解

  3 当公共建筑仅需在走道或回廊设置排烟时,其机械排烟量不应小于13000m³/h,或在走道两端(侧)均设置面积不小于2㎡的自然排烟窗(口)且两侧自然排烟窗(口)的距离不应小于走道长度的2/3。
    4 当公共建筑房间内与走道或回廊均需设置排烟时,其走道或回廊的机械排烟量可按60m³/(h·㎡)计算且不小于13000m³/h,或设置有效面积不小于走道、回廊建筑面积2%的自然排烟窗(口)。


第4款怎么理解,是所有房间均要开2%的窗吗?

我无窗房间之和小于200,无窗房间均小于50,走道大于20m,是按第3款还是第4款执行,如仅一个厕所(面积小于50)无窗,其它房间均有窗,走道自然排烟是两端2平,还是2%

消防网友62117 | 2023-11-06 11:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

whale 2023-11-07 10:33 00 [回复]举报

按第三条执行,开向走道的小于50的无窗房间可不设置排烟措施。

按第四条执行则需要开向走道的房间都需要满足2%的排烟窗要求。

如仅一个厕所(面积小于50)无窗,其它房间均有窗,走道自然排烟建议两端2平,如采用2%需和审图沟通(卫生间是否可不做排烟)。

潘天坤 2024-06-19 22:38 00 [回复]举报

第4款的理解为:功能房间当设置满足排烟要求的设施(机械排烟或者自然排烟均符合排烟要求),此时走道排烟可以设置建筑面积2%的自然排烟口。房间与走道均设置排烟,因为房间已经设置了排烟设施,所以走道排烟相对第3款放宽要求。

小于50平方米的房间,排烟口可以设置在疏散走道,排烟量按第3款计算。

建筑防烟排烟系统技术标准 GB51251-2017第4.2.12条第3款规定 :对于需要设置机械排烟系统的房间,当其建筑面积小于50㎡时,可通过走道排烟,排烟口可设置在疏散走道;排烟量应按本标准第4.6.3条第3款计算。