消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防设计审查项目,个人认为13#和15#符合两栋建筑防火间距不限的情形,2#和3#共用防火墙,实质上为一栋建筑的两个防火分区,不是两栋建筑,麻烦给点意见!

无名之辈 | 2023-11-01 08:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

胡胡203 2023-11-01 08:51 10 [回复]举报

13#、15#厂房防火墙分隔间距不限应该没有问题;至于2#、3#厂房,可以参照建筑设计说明,应该有明确是否两个不同建筑或者同一建筑的不同防火分区;或者参考平面图如果画在一起,也可以默认为同一建筑;或者参考规证。

无名之辈   回复: 胡胡2032023-11-01 09:09

0    0 [回复]举报

陈曲 2023-11-01 09:34 10 [回复]举报

同意审查意见

关闭

关闭

手机APP下载