丙二类多层厂房,耐火等级二级,是否可以不做自喷系统?

丙二类多层厂房,耐火等级二级,是否可以不做自喷系统?

WeiHL | 2023-10-28 13:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

我的是昵称 2023-10-30 14:16 00 [回复]举报

不能,耐火等级和防火间距有关,和是否做自喷没有太大的关联。一个是被动防火一个是主动灭火。按建规丙二类厂房占地面积大于1500平或总建筑面积大于3000平的就要自喷。

画图匠   回复: 我的是昵称2023-10-30 18:08

“占地面积大于1500平或总建筑面积大于3000平”这说的是丙类仓库——《建规》8.3.2.7。丙类厂房需要做自喷:一是高层乙丙类厂房、二是建筑面积超规范要求时增设——《建规》8.3.1.5 、8.3.3。另外,如果执行《精细规》(GB51283-2020 )的话,室内设有多层设备平台时,要按《精细规》8.2.5设置喷淋。

0    0 [回复]举报

毛胡子999 2023-11-03 16:08 00 [回复]举报

通规已废除了建规8.3.1的强制性,并规定了:

    2 地上占地面积大于1500㎡或总建筑面积大于3000㎡的单、多层制鞋、制衣、玩具及电子等类似用途的厂房;

    3 占地面积大于1500㎡的地上木器厂房;

    4 泡沫塑料厂的预发、成型、切片、压花部位;

    5 除本条第1款~第4款规定外的其他乙、丙类高层厂房;

以上厂房须设自灭系统,你对照上面是否涉及