消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

柴油为燃料的食堂,贴邻的一个房间里存放约1.5立方米容量的柴油,请问是否可行?

柴油为燃料的食堂,贴邻的一个房间里存放约1.5立方米容量的柴油,请问是否可行?

地精修补匠 | 2023-07-26 15:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-07-26 15:42 10 [回复]举报

建筑防火通用规范 GB55037-2022

4.1.4 燃油或燃气锅炉、可燃油油浸变压器、充有可燃油的高压电容器和多油开关、柴油发电机房等独立建造的设备用房与民用建筑贴邻时,应采用防火墙分隔,且不应贴邻建筑中人员密集的场所。上述设备用房附设在建筑内时,应符合下列规定:     1 当位于人员密集的场所的上一层、下一层或贴邻时,应采取防止设备用房的爆炸作用危及上一层、下一层或相邻场所的措施;     2 设备用房的疏散门应直通室外或安全出口;     3 设备用房应采用耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔,防火隔墙上的门、窗应为甲级防火门、窗。

4.1.5 附设在建筑内的燃油或燃气锅炉房、柴油发电机房,除应符合本规范第4.1.4条的规定外,尚应符合下列规定:     1 常(负)压燃油或燃气锅炉房不应位于地下二层及以下,位于屋顶的常(负)压燃气锅炉房与通向屋面的安全出口的最小水平距离不应小于6m;其他燃油或燃气锅炉房应位于建筑首层的靠外墙部位或地下一层的靠外侧部位,不应贴邻消防救援专用出入口、疏散楼梯(间)或人员的主要疏散通道。     2 建筑内单间储油间的燃油储存量不应大于1m³。油箱的通气管设置应满足防火要求,油箱的下部应设置防止油品流散的设施。储油间应采用耐火极限不低于3.00h的防火隔墙与发电机间、锅炉间分隔。     3 柴油机的排烟管、柴油机房的通风管、与储油间无关的电气线路等,不应穿过储油间。     4 燃油或燃气管道在设备间内及进入建筑物前,应分别设置具有自动和手动关闭功能的切断阀。

周家斌 2023-07-26 20:06 20 [回复]举报

不可以,可以分开两个储油间设置

关闭

关闭

手机APP下载