消火栓箱门开启角度要多少度?两个规范要求不同

消防给水及消火栓系统技术规范 GB50974-2014

12.3.10 消火栓箱的安装应符合下列规定:
    1 消火栓的启闭阀门设置位置应便于操作使用,阀门的中心距箱侧面应为140mm,距箱后内表面应为100mm,允许偏差±5mm;
    2 室内消火栓箱的安装应平正、牢固,暗装的消火栓箱不应破坏隔墙的耐火性能;
    3 箱体安装的垂直度允许偏差为±3mm;
    4 消火栓箱门的开启不应小于120°;


 消火栓箱 GB/T14561-2019

5.5.3 箱门的开启角度不应小于160°。

地精修补匠 | 2023-07-24 15:06
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-07-24 15:41 20 [回复]举报

50974是安装以后针对消火栓箱的验收要求


14561是针对消火栓箱这个产品本身进场的验收要求


阶段不一样,所以要求不一样,不冲突。

周家斌 2023-07-24 23:02 10 [回复]举报

一个是产品规范,一个是施工验收规范,不矛盾