组合分配式干粉灭火系统中的信号反馈装置必须安装在选择阀之后吗,就是选择阀之后的输粉管上


消防学徒 | 2023-07-18 19:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-07-19 08:59 00 [回复]举报

组合分配系统对应多个灭火区域,反馈装置安装在选择阀之后,这样可以知道灭火剂是否送达对应的灭火区域。

消防学徒   回复: 安洪全2023-07-19 11:28

有相应的规范吗,我提了这个问题,但设备厂家那通用规范上第一条说是为规定设置位置

0    0 [回复]举报

安洪全   回复: 消防学徒2023-07-19 13:26

干粉灭火系统设计规范 GB50347-2004

5.3.4 在通向防护区保护对象的灭火系统主管道上,应设置压力信号器或流量信号器。

条文说明:

5.3.4 设置压力信号器或流量信号器的目的是为了将灭火剂释放信号及释放区域及时反馈到控制盘上,便于确认灭火剂是否喷放。

0    0 [回复]举报

消防学徒   回复: 安洪全2023-07-20 07:32

好的,谢谢

0    0 [回复]举报