消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

医疗卫生对单位负一层设置餐厅使用天然气要求

租了一栋楼作为医院使用,在负一层开了一间280平米使用天然气的餐厅,餐厅没有独立的防火分区和排烟系统,请问这个餐厅是否符合防火规范,怎么要求的?

天选之子 | 2023-07-07 13:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-07-07 13:43 00 [回复]举报

建筑防火通用规范 GB55037-2022

4.3.12 建筑内使用天然气的部位应便于通风和防爆泄压。

同同不同 2023-07-07 16:08 00 [回复]举报

《建规》第6.2.3条规定,厨房应以2.00h防火隔墙和乙级防火门与其他部分分隔。明厨、明档,应设耐火极限不小于2.00h的防火隔墙或防火卷帘与餐厅分隔。

《火通规》第4.1.3 下列场所应采用防火门、防火窗、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.00h的楼板与其他区域分隔:
1 住宅建筑中的汽车库和锅炉房;
2 除居住建筑中的套内自用厨房可不分隔外,建筑内的厨房;

至于能不能置于地下,防火规范、燃气规范上应是未禁止,各地有地方规定,有些省份是禁止地下厨房采用明火或可燃气体的。

小马 2023-07-07 16:24 00 [回复]举报

肯定是不符合防火规范了,只有二百多平方是餐厅,没独立的防火分区可能涉及到同一建筑内有不同使用功能,应该要进行防火分隔的。有条件了找个当地设计院的咨询一下

关闭

关闭

手机APP下载