消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教,双连锁预作用系统压力开关和快速泄压阀的疑问

请问:

1.压力开关动作信号由什么控制,是系统侧压力和雨淋阀侧压力差,还是低压电接触压力表控制?

2.双连锁系统压力开关是接到火灾报警控制柜还是接到预作用控制盘?

3.双连锁预作用系统管网末端的快速泄压阀启动是在火灾控制柜给定火灾信号后,还是预作用电磁阀启动后?控制信号应该接到火灾控制柜还是预作用控制盘?

叶落 | 2023-06-29 08:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

同同不同 2023-06-29 11:30 00 [回复]举报

1,压力开关不是系统侧与供水侧的压力差,是由系统侧充压气体压力值控制,

2,预作用控制盘接到火报系统确认火灾及压力开关信号后启动预作用报警阀,

3,个人认为快排宜与报警阀组同时启动,由预作用控制盘控制

关闭

关闭

手机APP下载