消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

设备用房的设置

防排烟风机必须要设置设备用房嘛?


消防网友70379 | 2020-12-06 08:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

消防网友74957 2020-12-06 18:54 20 [回复]举报

4.4.5 排烟风机应设置在专用机房内,并应符合本标准第3.3.5条第5款的规定,且风机两侧应有600mm以上的空间。对于排烟系统与通风空气调节系统共用的系统,其排烟风机与排风风机的合用机房应符合下列规定:
    1 机房内应设置自动喷水灭火系统;

    2 机房内不得设置用于机械加压送风的风机与管道;
    3 排烟风机与排烟管道的连接部件应能在280℃时连续30min保证其结构完整性。

黄辉 2020-12-07 08:23 10 [回复]举报

参 建筑防烟排烟系统技术标准 GB51251-2017 


3.3.5 机械加压送风风机宜采用轴流风机或中、低压离心风机,其设置应符合下列规定:
5 送风机应设置在专用机房内,送风机房并应符合现行国家标准《建筑设计防火规范》GB 50016的规定。

4.4.5 排烟风机应设置在专用机房内,并应符合本标准第3.3.5条第5款的规定,且风机两侧应有600mm以上的空间。对于排烟系统与通风空气调节系统共用的系统,其排烟风机与排风风机的合用机房应符合下列规定:

周家斌 2022-05-09 13:26 10 [回复]举报

新规范规定的,必须要!

潘天坤 2024-06-18 17:03 00 [回复]举报

按照烟规GB51251要求,需要设置专用机房

不过考虑到规划面积或者既有建筑改造等,可能有些时候不好执行

很多地区的技术文件会对用挡雨措施或者防火板之类的替代,但是从烟规角度没有说可以替代

建议楼主结合地区技术文件和地区内设计、审查、检测等单位专家们意见综合考虑

李勤 2025-06-17 16:25 00 [回复]举报

关闭

关闭

手机APP下载