室外疏散楼梯疏散门开设的要求

根据建规GB50016-2014     6.4.5条的疏散门指的是通向楼梯间的疏散门吗?与室外楼梯的疏散门在小于2米的范围内开设通向室外的疏散门可以吗?周围小于2米的位置可以开防火窗吗?

6.4.5 室外疏散楼梯应符合下列规定:

1 栏杆扶手的高度不应小于1.10m,楼梯的净宽度不应小于0.90m。

2 倾斜角度不应大于45°。

3 梯段和平台均应采用不燃材料制作。平台的耐火极限不应低于1.00h,梯段的耐火极限不应低于0.25h。

4 通向室外楼梯的门应采用乙级防火门,并应向外开启。

5 除疏散门外,楼梯周围2m内的墙面上不应设置门、窗、洞口。疏散门不应正对梯段。

消防网友77957 | 2020-11-11 09:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

PQ 2020-11-11 13:30 10 [回复]举报

1、6.4.5条的疏散门指的是通向楼梯间的疏散门;

2、小于两米范围内,按图示首层不可开设通向室外的疏散门,但是建规设施指南图6.34有不同表达;

3、参考建规实施指南观点:周围2米范围内除疏散门外,不应有其他洞口,必须开设的洞口应设置窗扇不可开启的防火窗,其耐火极限不低于所在外墙的耐火极限。