消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑防火通用规范里关于丁类厂房的消防给水的一些疑问

各位老师想请教下:

1. 新的建筑防火通用规范6.1号就要实施了。里面8.1.7:“建筑占地面积大于300㎡的甲、乙、丙类厂房需要设置室内消火栓系统”,不包含丁类厂房了。按照新规,丁类厂房是否可以不设置室内消火栓了?

2. 新的建筑防火通用规范废除了建规的8.2.1,但是没有废除8.2.2。如果丁类厂房,按照新规不需要设室内消火栓,那是否还需要设置消防软管卷盘或轻便消防水龙?

3. 另外,对于丁类厂房附设的办公楼,虽然建筑会按照规划指标限值将其定义成厂房,但我们水消防一般会按办公来做。如果是这么做的话,是否附设的办公楼达到新规的办公建筑要求后还是要设置室内消火栓和喷淋,但是厂房区域就不需要设置室内消火栓了?


谢谢老师赐教!

HOHO | 2023-02-16 14:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

永锅 2023-02-16 15:37 00 [回复]举报

新规范对老规范强条及非强条条文不合理的部分进行删除、补充和完善,未涉及的部分按老规范执行。

丁类厂房,按照新规不需要设室内消火栓,应按老规范设置消防软管卷盘或轻便消防水龙。

为厂房服务的附属用房根据其具体的使用功能来进行消防设计。

比如:宿舍楼、食堂等,宿舍楼根据建筑规模需要设置喷淋的要设置喷淋系统,食堂为人员密集场所的要在消火栓箱内设消防软管卷盘或轻便消防水龙等。

HOHO   回复: 永锅2023-02-17 16:17

谢谢老师解答!

0    0 [回复]举报

消防黄河 2023-02-18 08:08 10 [回复]举报

1.是;2.耐火等级为一二级且体积小于3000立方米时不需要,耐火等级为三四级或体积大于3000立方米时宜设置;3.是。

HOHO   回复: 消防黄河2023-02-19 11:36

谢谢老师的解答。

再不耻下问一下,新的消防设施通用规范3.0.5-3: 在设置室内消火栓的场所内,包括设备层在内的各层均应设置消火栓。

按此条理解,丁类厂房和附设办公楼建筑定性为一栋建筑,在办公楼设置了消火栓后厂房是不是也被迫要设置消火栓?(本人理解为一栋建筑如果一部分要设置消火栓,那其余部分就也要设置。但喷淋可以根据各区域的实际使用功能来分开设置。不知理解是否正确,请老师指教,谢谢!)

0    0 [回复]举报

关闭

关闭

手机APP下载