储烟仓问题

场所净高2.6m的会议室,根据烟规4.6.9和4.6.1条,储烟仓是不是可以按1.1m高度去计算机械排烟?设计清晰高度1.5m会不会影响人员疏散

乌云 | 2022-11-10 09:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

aalwbw 2022-11-10 17:48 00 [回复]举报

不会影响疏散的。

理由是:4.6.9 走道、室内空间净高不大于3m的区域,其最小清晰高度不宜小于其净高的1/2(净高2.6米,最小清晰高度为1.3米,1.5>1.3,满足规范要求。);