消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外取水口是否可以取代一路市政进水

3栋一类高层住宅建筑,地下室负一层汽车库和设备房,只设计一路市政进水,在室外设置一个消防取水口,是否可满足要求?

小曾 | 2022-09-19 17:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防黄河 2022-09-19 21:50 00 [回复]举报

需要两路供水,您所述取水口是从哪里取水的口?水池?水井?

小曾   回复: 消防黄河2022-09-20 10:22

消防取水口从地下室消防水池取水,但室外消火栓(20L/S)与室内消火栓合用临时高压给水系统,那市政进水还是需要两路吗?

0    0 [回复]举报

周家斌   回复: 小曾2022-09-20 14:15

所描述的情况在消防水池容积符合室内外总消防用水量,可以不用两路市政水源。

0    0 [回复]举报

小曾   回复: 周家斌2022-09-20 15:11

收到,感谢

0    0 [回复]举报

小曾   回复: 小曾2022-09-20 15:12

感谢

0    0 [回复]举报

消防黄河   回复: 小曾2022-09-21 17:13

就因为市政一路供水,不满足两路,才设置了消防水池。如果市政两路,且流量满足要求,就不用设置水池了。

0    0 [回复]举报

关闭

关闭

手机APP下载