消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问弱电机房属于配电间范畴吗?

如果弱电机房也属于配电间范畴,依据规范要做甲级防火门;如果不属于有无依据?

螺旋 | 2022-07-29 08:56
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

ZZS 2022-07-29 10:23 20 [回复]举报

参考《民用建筑电气设计标准 GB51348-2019》

23.6.2    弱电间墙体应为耐火极限不低于1.0h 的不燃烧体,门应采用丙级防火门。

周家斌 2022-08-01 11:47 00 [回复]举报


关闭

关闭

手机APP下载