什么是小型公共建筑?建规8.1.3的解释中出现了“小型公共建筑”一词,谢谢。



8.1.3 本条为强制性条文。水泵接合器是建筑室外消防给水系统的组成部分,主要用于连接消防车,向室内消火栓给水系统、自动喷水或水喷雾等水灭火系统或设施供水。在建筑外墙上或建筑外墙附近设置水泵接合器,能更有效地利用建筑内的消防设施,节省消防员登高扑救、铺设水带的时间。因此,原则上,设置室内消防给水系统或设置自动喷水、水喷雾灭火系统、泡沫雨淋灭火系统等系统的建筑,都需要设置水泵接合器。但考虑到一些层数不多的建筑,如小型公共建筑和多层住宅建筑,也可在灭火时在建筑内铺设水带采用消防车直接供水,而不需设置水泵接合器。


zjs | 2022-06-16 13:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-06-11 17:12 00 [回复]举报

符合单、多层标准且不大于5层的公共建筑、

zjs   回复: 周家斌2022-06-13 13:35

能给个这句话的出处吗?谢谢

0    0 [回复]举报

充楞装傻 2022-06-16 14:34 00 [回复]举报

跟8.1.3的 

    1 超过5层的公共建筑;
    2 超过4层的厂房或仓库;
    3 其他高层建筑;
    4 超过2层或建筑面积大于10000m²的地下建筑(室)。

属于公建范围的都反过来就是了~

1 不超5层

3 非高层公建(24米)

4 不超过2层且建筑面积小于1万的地下公共建筑。

zjs   回复: 充楞装傻2022-06-28 17:07

8.1.3 自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统和固定消防炮灭火系统等系统以及下列建筑的室内消火栓给水系统应设置消防水泵接合器:
    1 超过5层的公共建筑;
    2 超过4层的厂房或仓库;
    3 其他高层建筑;
    4 超过2层或建筑面积大于10000m²的地下建筑(室)。

8.1.3告诉我两层意思:1、自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统和固定消防炮灭火系统等系统应设置消防水泵接合器。我想说是不是跟8.1.3的解释“但考虑到一些层数不多的建筑,如小型公共建筑和多层住宅建筑,也可在灭火时在建筑内铺设水带采用消防车直接供水,而不需设置水泵接合器。”相矛盾啊?谢谢

                     