同一防火分区里,只靠两个手报能不能作为联动启动信号

同一防火分区两个烟感或一个烟感加手报可以作为联动促发信号么

天天消防 | 2022-05-19 09:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

刘丽波 2022-05-19 22:41 00 [回复]举报

看联动那个系统,防烟系统可以。排烟系统需要同一防烟分区的联动触发信号。

消防小学生刘振 2022-06-07 17:25 00 [回复]举报

两个手报不能做为联动启动信号,规范没有此种启动方式,同时考虑到现场实际情况两个手报做为联动启动信号存在误动作隐患,容易误触发火警联动,同一防火分区两个烟感或一个烟感加一个手报是规范要求的标准联动触发方式,当然可以作为联动触发信号。

珍珠baby 2022-06-21 15:14 00 [回复]举报

两个手报是不行的,手报因为安装位置,误报的可能性大。两个火灾探测器或者一探测器加一手报是可以的。不过烟感和温感有的地方也是有区别的。比如预作用报警 是烟感 ,雨淋系统是温感