丙类厂房能不能用木结构屋顶?

老师您好,该建筑原来设计用途是玻璃加工,单层,砖木结构,混凝土柱,木结构承重屋顶,现欲将厂房改变成服装加工车间。

根据《建筑设计防火规范》,丙类厂房耐火等级不应低于三级,屋顶称重构件满足难燃0.5小时即可。

但依据《木结构建筑通用规范》,丙类厂房不能采用木结构建筑或木结构组合建筑。


因此,想问,该厂房应该适用哪一条规范,木质屋顶称重构件算不算木结构组合建筑。

秦亚龙注消 | 2022-03-26 14:56
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

法亦有道 2022-03-27 22:40 00 [回复]举报

一、根据《建筑设计防火规范》GB50016-2014(2018年版) 第3.2.3条,当为建筑面积不大于500m²的单层丙类厂房可采用三级耐火等级的建筑。

二、请确认一下《木结构建筑通用规范》制定时间、适用范围;

三、《木结构建筑通用规范》应该属于特别规定。

林继青 2022-03-28 08:43 00 [回复]举报

三级耐火等级要求承重结构为难燃材料,木结构是可燃材料,不做任何处理当然是不能用的

充楞装傻 2022-03-28 10:12 00 [回复]举报

不能。 木顶~可燃,是4级。与《木结构建筑通用规范》一致.