消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

甲类中间库能够放在多层丁类厂房的2层?

根据《建筑设计防火规范》GB50016-2014(2018年版)中关于中间仓库设置的要求:3.3.6 厂房内设置中间仓库时,应符合下列规定:1 甲、乙类中间仓库应靠外墙布置,其储量不宜超过1昼夜的需要量;  2 甲、乙、丙类中间仓库应采用防火墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔; 3 丁、戊类中间仓库应采用耐火极限不低于2.00h的防火隔墙和1.00h的楼板与其他部位分隔;4 仓库的耐火等级和面积应符合本规范第3.3.2条和第3.3.3条的规定。而根据第4款中第3.3.2表3.3.2中,只对甲类单层仓库进行面积要求,而对甲类多层仓库是不允许的;而参照 建规3.6.7条,“厂房内有爆炸危险性的甲乙类生产部位,宜布置在单层厂房靠外墙的泄压设施或多层厂房顶层靠外墙的泄压设施附近”,依据此条说明高危险类别的房间布置在顶层更有利于结构安全及泄爆,设置在首层反而不利于建筑结构安全及泄爆。这样看来,甲类中间仓库放在顶层考外墙应该更安全,更合理?

wangy | 2022-03-21 09:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

法亦有道 2022-03-21 21:20 00 [回复]举报

1、甲、乙类中间仓库对储量有要求,不宜超过1昼夜的需要量;

2、厂房内有爆炸危险性的甲乙类生产部位,宜布置在单层厂房靠外墙的泄压设施或多层厂房顶层靠外墙的泄压设施附近”,该规定是针对生产部位,不要和储存相混淆;

wangy   回复: 法亦有道2022-04-05 22:09

如果是甲类的中间库,放置的量不超过一昼夜。虽然“厂房内有爆炸危险性的甲乙类生产部位,宜布置在单层厂房靠外墙的泄压设施或多层厂房顶层靠外墙的泄压设施附近”是针对厂房而言的,但是是否从另外一个方面说,放在顶层来说,是否更安全?

0    0 [回复]举报

沐浴阳光 2022-03-22 11:05 00 [回复]举报

    甲类中间仓库不应设置在多层厂房内,如果设置,该厂房宜为单层。

wangy   回复: 沐浴阳光2022-04-05 22:13

为什么甲类中间库不能放在多层厂房内?规范中条文说明也提到了关于钟表厂内放置汽油的问题,这也说明了甲类中间库可以放在丁类厂房内。但是为什么就不能放在多层厂房内呢?

0    0 [回复]举报

关闭

关闭

手机APP下载