消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑高度大于50米小于100米的公寓式办公楼的性质

1-3层为商业建筑,4-18层为公寓式办公楼,建筑高度大于50米小于100米,此中建筑应该划分为什么类型的建筑,是一类高层公共建筑还是二类高层公共建筑,又或者为一层高层住宅建筑

半知半解 | 2022-02-11 11:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

刘丽波 2022-02-11 12:52 00 [回复]举报

一类高层公共建筑

半知半解   回复: 刘丽波2022-02-11 15:34

原一次设计的时候为公寓楼,现进行二次装修改造设计为公寓式办公建筑的话也为一类高层公共建筑么;现二次设计的时候设计院在3#楼设立一个为18立方米的水箱。如果是一类高层公共建筑最少需要36立方米,如果是二类高层公共建筑或者一类高层住宅18立方米就可以

0    0 [回复]举报

牛疼   回复: 半知半解2022-03-01 11:20

参照gb50016 5.1.1

0    0 [回复]举报

刘丽波   回复: 半知半解2022-03-01 14:59

除非上面是住宅,高位消防水箱才是18T。

0    0 [回复]举报

星林夜语 2022-02-11 12:54 00 [回复]举报

商业和办公楼都是公共建筑,高度大于50米小于100米,应该是一类公共建筑。不属于住宅建筑。如果住宅建筑和非住宅为同一建筑内,就应该按5.4.10.3条要求考虑消防设计。

郭子123 2022-02-11 13:33 00 [回复]举报

一类高层公共建筑

小凤姐 2022-03-02 16:35 00 [回复]举报

超过50米的公共建筑,一类高层公共建筑,水箱不应小于36m³

关闭

关闭

手机APP下载