七氟丙烷可以靠自己压力开启选择阀吗?

一些自压式气体灭火系统可以不用启动气体瓶组的压力开启选择阀,而靠自身压力开启选择阀。(系统启动后,气体在选择阀前管道聚集并达到一定压力后会自动开启选择阀),七氟丙烷可以这样开启选择阀吗?

大暑 | 2021-11-30 09:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

黄辉 2021-12-28 09:30 00 [回复]举报

假定七氟丙烷靠自身压力可以打开选择阀,那么有以下问题:

1 组合分配系统,有多个选择阀,如果用灭火剂瓶组自身压力启动选择阀,那么所有的选择阀都会被打开。

2 与规范5.0.9的要求不符。“5.0.9 组合分配系统启动时,选择阀应在容器阀开启前或同时打开。" 

吴俊 2021-12-28 17:02 00 [回复]举报

不可以用自身压力打开选择阀,确实会造成当有多个防护区时全部打开的情况;当只有一个保护区时也可能造成误动作的情况