消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

机械排烟系统排烟风口、排烟防火阀的设置与联动控制

建筑内走道设置机械排烟系统,系统在平层风管入口处设置有280℃常开排烟防火阀,排烟口采用百叶口(3个风口在同一防烟分区内),风口未设置排烟阀,在这种情况下,1、排烟口能否不设置排烟阀,采用百叶口?2、联动控制逻辑关系能不能采用 同一防烟分区内2个火警点联动关闭除报警区域楼层以外的其他楼层设置的280℃排烟防火阀?

全都是泡沫 | 2021-09-24 16:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

刘丽波 2021-09-25 19:37 00 [回复]举报

此系统图采用常开的百叶口是不合适的。二个方案,方案一,在每层的排烟防火阀后面集中加一个总排烟阀;方案二将常开排烟口改为常闭的板式排烟口或多叶排烟口。如排烟风机仅负责一个防烟分区排烟可以排烟防火阀后加常开的排烟口形式。其联动控制应符合《火灾自动报警系统设计规范》。排烟防火阀没有联动关闭功能,只有温度达到280℃熔断器关闭功能。

l123   回复: 刘丽波2023-06-06 14:51

老师,如果排烟风机仅负责一个防烟分区的排烟,设置百叶风口,不设置排烟阀。对于烟规的第5.2.2条的强规里第4小条:系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动。由于没有排烟阀或排烟口,这一条还需要执行吗?

0    0 [回复]举报

潘天坤   回复: l1232024-07-01 17:45

这个区域不需要设置手动开启装置(火灾时由火灾自动报警系统联动开启排烟区域的排烟阀或排烟口,应在现场设置手动开启装置),既然不需要设置手动开启装置,那更不用说要求打开手动装置风机要可以启动

话说回来,本来此位置的排烟口就是常开的,规范里也没有要求如何实现这个功能,可以通过确认火灾后联动启动风机来解释本条款,从规范来说并没有违反此条款内容

最后再说下,地下室电动车充电桩区域一般会设置手动开启装置,设置手动装置的区域一般能够实现要求

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

0    0 [回复]举报

一片冰雨 2021-09-25 22:31 00 [回复]举报

这个样子节省不了多少,反倒是不符合规范要求,遇到较真的验收人员还得费半天的口舌关键是不一定能通过!返工才是最痛苦的事!

阳明心 2023-04-14 11:07 00 [回复]举报

每层3个排烟口为一个防烟分区,所以排烟风机负担了5个防烟分区,考虑火灾时一般启动三个楼层排烟,所以应该每个风口装阀或楼层总风管装阀。

如果考虑火灾时15个风口同时排烟,就要增加风机和风管风量,增加投入,没有必要。

潘天坤   回复: 阳明心2024-07-01 17:39

火灾时为什么启动三个楼层排烟?

0    0 [回复]举报

潘天坤 2024-07-01 17:37 00 [回复]举报

1、此时如果不设置排烟阀,则排烟口为常开,一启动则所有排烟口均启动,这样子风机风量不够用了(原本计算排烟量只考虑相邻两个防烟分区)

2、能否采用,要看功能能否实现,不知道市面上是否有这类产品,不知道是否可以实现相关功能

关闭

关闭

手机APP下载