地下排烟系统的室外排烟口可否加装自垂百叶、止回阀、或电动风阀防止外界风在排烟风机未启动时倒灌回风

如题如图地下排烟系统的室外排烟口可否加装自垂百叶、止回阀、或电动风阀等措施防止外界风在排烟风机未启动时倒灌回风。有无相关文献或规范明确规定是否可以加装或明确规定不能加装?

消防网友67152 | 2021-06-24 07:31
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

剑胆琴心 2022-01-11 08:32 00 [回复]举报

《建筑防烟排烟技术标准》第4.4.8 排烟管道的设置和耐火极限应符合下列规定:  1 排烟管道及其连接部件应能在280℃时连续30min保证其结构完整性。。排烟出口系排烟管道的一部分,应保证其耐火完整性。通常说的的风阀及单向阀一般不能满足耐火完整性要求而多用于通风管道,当通风排烟管道合用时从耐火完整性出发不建议在排烟管道出口设置单向阀或者风阀,日常倾向于自垂式百叶。以上供参考