请问一下,喷水立管这样设置是否可以

消防小萌新 | 2025-06-24 13:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

罗马苏丹 2025-06-24 14:10 00 [回复]举报

压力能满足就行,不过一般是从干管接出,不会这样接

懒得说 2025-06-24 14:41 00 [回复]举报

在风管下方增设喷头有这种做法,上下喷头按照一个喷头流量计算。

小唐12321 2025-06-24 15:13 00 [回复]举报

可以


牛丫头消防课堂 2025-06-24 18:04 00 [回复]举报

第一,DN25的管子上带了2个喷头,不符合《自动喷水灭火系统设计规范》 GB50084-2017第8.0.9条;

第二,吊架距离末端喷头超过750mm,不符合《自动喷水灭火系统施工及验收规范》 GB50261-2017第5.1.15条规定;


消防小萌新   回复: 牛丫头消防课堂2025-06-25 23:22

谢谢张老师,非常感谢您!

0    0 [回复]举报

李勤 2025-06-26 07:56 00 [回复]举报

只要喷头上端支管,管径满足要求就可以。