请问各位老师,吊顶下的火灾探测器这样设置是否可以

请问各位老师,吊顶下的火灾探测器这样设置是否可以, 格栅吊顶上方还有空间,探测器旁边贴着的不是墙,是吊顶靠近墙边乡下突出的一块石膏板,谢谢

消防小萌新 | 2025-06-20 11:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

LD 2025-06-20 11:22 10 [回复]举报

6.2.18 感烟火灾探测器在格栅吊顶场所的设置,应符合下列规定:      1 镂空面积与总面积的比例不大于 15% 时,探测器应设置在吊顶下方。      2 镂空面积与总面积的比例大于 30% 时,探测器应设置在吊顶上方。      3 镂空面积与总面积的比例为 15%~30% 时,探测器的设置部位应根据实际试验结果确定。

消防小萌新   回复: LD2025-06-21 11:28

谢谢老师

0    0 [回复]举报

李勤 2025-06-20 12:27 10 [回复]举报

牛丫头消防课堂 2025-06-20 12:33 00 [回复]举报

你这个很明显,镂空率超过30%,应安装在吊顶上方(吸顶安装)

消防小萌新   回复: 牛丫头消防课堂2025-06-21 11:28

谢谢老师

0    0 [回复]举报

EHS专家-DL 2025-06-20 17:15 00 [回复]举报

镂空率30%以上,应该安装在吊顶上方,另外探测器周围 ‌0.5m范围内不应有遮挡物‌(包括墙体、梁、支架或您所述的突出石膏板)。

消防小萌新   回复: EHS专家-DL2025-06-21 11:28

谢谢老师

0    0 [回复]举报