配电室需要设置消火栓吗?

工厂配电室,面积超300平,可以不做室内消火栓吗?

我是小鱼鱼 | 2025-06-16 17:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

小唐12321 2025-06-16 17:32 00 [回复]举报

配电房内就不能设置消火栓,管道漏水怎么办。

潘天坤 2025-06-16 17:46 00 [回复]举报

可能需要看建筑是否需要设置室内消火栓系统,如果配电室设置在建筑内,并且此建筑属于需要设置室内消火栓系统的场所,那么配电室一般要满足充实水柱同时达到任何部位的要求(具体几股充实水柱要看规范要求)


如果是独立建造的配电室,那么要看此配电室的火灾危险性和建筑面积,建筑占地面积大于300平方米的甲、乙、丙类厂房需要设置室内消火栓系统,其他情况可以不设置室内消火栓系统


当满足上述设置室内消火栓系统情况,一般要满足充实水柱同时达到任何部位的要求(具体几股充实水柱要看规范要求),室内消火栓可以设置在门外


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准





牛丫头消防课堂 2025-06-16 18:23 00 [回复]举报

依据《火力发电厂与变电站设计防火标准》 GB50229-2019

一般设置在楼梯间或走廊,很少设置在配电室内。

变电站的规划和设计,应同时设计消防给水系统。消防水源应有可靠的保证。
注:变电站内建筑物满足耐火等级不低于二级,体积不超过3000m³,且火灾危险性为戊类时,可不设消防给水。

喧哗 2025-06-17 08:30 00 [回复]举报

按GB50229火力发电和变电站规范,有关于变电站建筑室内消火栓的规定

EHS专家-DL 2025-06-17 08:32 00 [回复]举报

若原工厂设置有室内消火栓,该配电室应该也需要设置室内消火栓的。根据《消防给水及消火栓系统技术规范 GB50974-2014》7.4.3 设置室内消火栓的建筑,包括设备层在内的各层均应设置消火栓。

重庆消防 2025-06-17 08:45 00 [回复]举报

配电室属于丙丁类厂房,若是属于丙类,占地面积超过300m²,应设置室内消火栓;

若是属于丁类,则不需要设置室内消火栓。


罗马苏丹 2025-06-17 09:12 00 [回复]举报

需要的,面积超过300平米的厂房和仓库应设置室内消火栓。

萨曼岛的工程师 2025-06-17 11:16 00 [回复]举报

按照《通规》,超过面积要求应设,可以选择干式。

垚燊 2025-06-17 18:22 00 [回复]举报

配电房内不适合用水灭火,建议设置气体灭火系统