消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

高度大于12m的空间场所宜同时选择两种及以上火灾参数的火灾探测器(消防水炮带红外探测)

大佬们求教。专家提出丙类仓库大于12米高宜设置两种及以上参数的火灾探测器,我现在设置了线型光束感烟探测器,水专业设置的消防水炮。水炮自带红外紫外探测装置,可以作为第二种火灾参数的探测器吗,我还需要单独设置火焰探测器吗。

木叶 | 2025-06-10 13:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

罗马苏丹 2025-06-10 14:08 20 [回复]举报

不可以,消防水炮的红外紫外探测装置主要目的是定位火源,为水炮喷水灭火做准备,虽然也能探测到火源,但在火灾报警的精度、信号传输效率和准确性等方面不如专门的火焰探测器

牛丫头消防课堂 2025-06-10 21:53 30 [回复]举报

我个人认为可以,理由如下:

第一,依据《火灾自动报警系统设计规范》 GB50116-2013第12.4.1条,高度大于12m的空间场所宜同时选择两种及以上火灾参数的火灾探测器。

宜的条款不是必须设置。如果要设置,要考虑可靠性和经济性,现有的线型光束探测器作为主要的探测装置,用火焰探测器作为后备。

第二,依据《自动跟踪定位射流灭火系统技术标准> GB51427-2021第4.3.5 条,控制主机应具有与火灾自动报警系统和其他联动控制设备的通信接口。

所以该系统的火警可以传递至火灾报警系统,技术上很容易实现;(工程中多数没这么做)

李勤 2025-06-12 08:09 10 [回复]举报

首先规范是宜设置,不是强制条款。第二,线性光束和水炮红外紫外探测器,也能算作两种报警设备。

关闭

关闭

手机APP下载